I plan to install a 5kw wind turbine for grid connection. I heard that the inverter needs to comply with G83/1 regulation. The seller shows me one. But I found it is issued by the manufacturer on its own.
Is this ok? I suppose it should be tested by a third party, some certified body, right?
Come by this forum, hope get help here.
wind turbine grid connection: G83 problem
Moderator: Peak Moderation
- emordnilap
- Posts: 14815
- Joined: 05 Sep 2007, 16:36
- Location: here
- adam2
- Site Admin
- Posts: 10894
- Joined: 02 Jul 2007, 17:49
- Location: North Somerset, twinned with Atlantis
I believe that grid tie inverters are "self certified" and that provided it is ofrom a well known supplier, that this should present no problem.
Before spending any money I would obtain full details of the inverter that you propose to use, and obtain the written approval of your electricity supplier regarding this.
Before spending any money I would obtain full details of the inverter that you propose to use, and obtain the written approval of your electricity supplier regarding this.
"Installers and owners of emergency diesels must assume that they will have to run for a week or more"
Thanks Janco2, is your wind boy 6000A 's G83 certificated is issued by SMA itself?
That's too expensive for me. And the turbine i am planning to buy is already equipped with a griedtied inverter. But not sure if its G83 certificate is acceptable.
That's too expensive for me. And the turbine i am planning to buy is already equipped with a griedtied inverter. But not sure if its G83 certificate is acceptable.
Janco2 wrote:We have a grid connected 6kW wind turbine.
To enable us to obtain a grant, Ofgem sent us a form on which there was a list of equipment that they would accept for grid connection.
Regarding the G83 there was a list of compliant inverters.
Ours is a SMA Windy Boy 6,000A
Don't know whether SMA have certified it themselves.
Have a look at what it says on here:-
http://www.thebiggreenidea.org/images/b ... Energy.pdf
Sorry can't seem to get the above link to work properly
Basically, it seems you need agreement with the local Distribution Network Operator (DNO).
Part of the regulatory compliance is that any inverter has to be capable of monitoring grid voltage and closing down automatically when grid goes down.
There needs to be an On/off switch that can be padlocked in the Off position.
You will need a schematic of your installation and a copy of the electrical engineer's commissioning certificate before you go 'live'.
The latter is a big drawback as whenever the grid is down your installation will be unuseable too
Hope this helps. Perhaps contacting Ofgem would be useful as we think they have information about G83 compliance inverters.
Have a look at what it says on here:-
http://www.thebiggreenidea.org/images/b ... Energy.pdf
Sorry can't seem to get the above link to work properly
Basically, it seems you need agreement with the local Distribution Network Operator (DNO).
Part of the regulatory compliance is that any inverter has to be capable of monitoring grid voltage and closing down automatically when grid goes down.
There needs to be an On/off switch that can be padlocked in the Off position.
You will need a schematic of your installation and a copy of the electrical engineer's commissioning certificate before you go 'live'.
The latter is a big drawback as whenever the grid is down your installation will be unuseable too
Hope this helps. Perhaps contacting Ofgem would be useful as we think they have information about G83 compliance inverters.
G83/1 is single phase 240v micro generation
up to 3.7kw 16amp
G59/1 is three phase 415v systems
yours is in a slight grey area
5kw grid turbines with good outputs can produce up to 9kw
good inverter supplier can provide testing to ALL world standards
and provide test certificates in writing
UK G83/1 , G59/1
GERMANY VDE126
USA UL1741
OZ AS4771
TUV CE KEMA DK EN IEEE ISO etc
can if required supply global inverter
5kw input - max output 13kw 240v SP or 415v TP
with 5 years warranty
remember to fit ofgem approved import/export meters
and padlockable isolator and drawings with your application
up to 3.7kw 16amp
G59/1 is three phase 415v systems
yours is in a slight grey area
5kw grid turbines with good outputs can produce up to 9kw
good inverter supplier can provide testing to ALL world standards
and provide test certificates in writing
UK G83/1 , G59/1
GERMANY VDE126
USA UL1741
OZ AS4771
TUV CE KEMA DK EN IEEE ISO etc
can if required supply global inverter
5kw input - max output 13kw 240v SP or 415v TP
with 5 years warranty
remember to fit ofgem approved import/export meters
and padlockable isolator and drawings with your application